I recently installed a service to a residential log cabin. Since the breaker box was 15 feet away from outside wall, I installed a 200 amp disconnect switch under the meter. From the disconnect, I installed 2-#4/0 and 1-#2/0 for the ground. The power company refused to hook up because they said that I needed to add and additional bonding conductor from the disconnect to the breaker box. Is this correct?