Hi Everyone,
I am new to this forum. I am a junior engineer so please pardon me for the basic questions.
I have a 2MVA 25kV/600v Y-Y transformer. The secondary neutral is resistor grounded 5A. The client requires that our main incoming on our MCC be service entrance rated. The MCC vendor has quoted a Four Wire main incoming section and a Three wire MCC. The questions are as follows :
1. Does service entrance just mean that a neutral lug or neutral bus is provided in the main incoming?
2. I was going to run seven runs of 3c 750mcm cables for the secondary. The Wye point of the transformer would connect to the NGR which in turn will be grounded to the MCC ground bus. Is it okay to leave the neutral bus on the main incoming section unconnected to anything? It would basically be not in use. Based o. My understanding this shouldn't be a problem.
3. The vendor shows the neutral bus as tied to ground on the main incoming. Is this ok? I also have a surge arrestor and power meter. The vendor shows the neutral wired to both devices. Is this going to be an issue with the Surge arrestor since the neutral is tied to ground in the vendor drawings? What would the meter see if nothing is Connected to the neutral?
I hope I have explained things properly. Thank you in advance
I am new to this forum. I am a junior engineer so please pardon me for the basic questions.
I have a 2MVA 25kV/600v Y-Y transformer. The secondary neutral is resistor grounded 5A. The client requires that our main incoming on our MCC be service entrance rated. The MCC vendor has quoted a Four Wire main incoming section and a Three wire MCC. The questions are as follows :
1. Does service entrance just mean that a neutral lug or neutral bus is provided in the main incoming?
2. I was going to run seven runs of 3c 750mcm cables for the secondary. The Wye point of the transformer would connect to the NGR which in turn will be grounded to the MCC ground bus. Is it okay to leave the neutral bus on the main incoming section unconnected to anything? It would basically be not in use. Based o. My understanding this shouldn't be a problem.
3. The vendor shows the neutral bus as tied to ground on the main incoming. Is this ok? I also have a surge arrestor and power meter. The vendor shows the neutral wired to both devices. Is this going to be an issue with the Surge arrestor since the neutral is tied to ground in the vendor drawings? What would the meter see if nothing is Connected to the neutral?
I hope I have explained things properly. Thank you in advance