Can someone explain or point me to a good reference as to why the 120V single phase loads on a center tapped delta transformer secondary are limited to 5%? From what I have seen it based on circulating currents in the delta winding caused by unbalanced loads on the neutral of the transformer.
I'm looking at a particular application where this type of transformer is going to be used and have aprox 20kVA of single phase loads that will be added to this 480-240/120V transformer. Does this mean that the minimum transformer size that needs to be used is 400kVA? This seems really large for only 20kVA of single phase load. Total kVA connected to transformer is only 45kVA with about 20kVA on the center tapped winding (10kVA on each side of tap) Originally I thought a 75kVA transformer would cut it with about 12.5kVA on the untapped phases and 20kVA on the center tapped phase but now with the 5% rule its looking like I need a much large transformer.
Should I stick with a center tapped delta, or use some other winding configuration where circulating currents are not an issue.
I'm looking at a particular application where this type of transformer is going to be used and have aprox 20kVA of single phase loads that will be added to this 480-240/120V transformer. Does this mean that the minimum transformer size that needs to be used is 400kVA? This seems really large for only 20kVA of single phase load. Total kVA connected to transformer is only 45kVA with about 20kVA on the center tapped winding (10kVA on each side of tap) Originally I thought a 75kVA transformer would cut it with about 12.5kVA on the untapped phases and 20kVA on the center tapped phase but now with the 5% rule its looking like I need a much large transformer.
Should I stick with a center tapped delta, or use some other winding configuration where circulating currents are not an issue.