Question for an electrical engineer
I'm using Fluke 1654B multi tester to perform loop test from the furthest outlet.
The meter gives me the total impedance on the circuit all the way to the utility
Transformer. The code in general wants us keep everything below 5% vd. So if my math is correct and my way of thinking would be any value of impedance to and including 5 ohms or less would equal % of voltage drop.
Eg. 3 ohms impedance reading would equal 3% vd,
A 5 ohm reading would 5 % vd
A 20 ohm read would be 20% an so on...
THE CIRCUIT READS A STEADY123 VOLTS BEFORE APPLYING BEFORE APPLYING THE VD,
Mathematically when you convert total impedance to equal percent voltage drop it seems to work
Look forward to you comments