5 wire system in a condo

Status
Not open for further replies.
I inspected a 5 wire system, black, blue, red, green, and white today in the sub panel of a condo and the green (equipment ground bus bar) is bonded to the panel with a strap. Is this ok? Thanks.
 
It's required for the panel enclosure to be bonded to the EGC. It's prohibited for anything else in a subpanel to be bonded, including the neutral.
 
I thought so but wanted to double check. Why would there be 5 wires? I have not seen 5 before. Thank you for your help!

Sounds like you are describing a 208/120 Y 3 phase feeder. Not real common to run 3 phase feeders to condos but I've seen it done.
 