50/50A spa hook up

Status
Not open for further replies.

jute

Senior Member
Location
SO CAL
I have a 50/50A 2 pole breaker installed in a 200a main panel... I used 3/4" thinwall conduit from the panel down to a 3/4" LB, I put a romex connector on the end of the LB and ran 50' of 8/3 with a #10 ground romex out to a 4x4 sq wp j-box mounted on the exterior of the house for an above ground spa hook up and from there I came out with a 6' whip of 3/4" seal tite to be hard wired to the spa. My question is can I fit 6/3 with ground in the existing 3/4" conduit. I used 8/3 with #10 ground and need to replace with 6/3 with #?ground. Also can I just strip back the romex and feed it through the seal tite so I can just run it through the 4x4 wp j-box and the seal tite?? Thanks, JB
 
jute said:
I have a 50/50A 2 pole breaker installed in a 200a main panel... I used 3/4" thinwall conduit from the panel down to a 3/4" LB, I put a romex connector on the end of the LB and ran 50' of 8/3 with a #10 ground romex out to a 4x4 sq wp j-box mounted on the exterior of the house for an above ground spa hook up and from there I came out with a 6' whip of 3/4" seal tite to be hard wired to the spa. My question is can I fit 6/3 with ground in the existing 3/4" conduit. I used 8/3 with #10 ground and need to replace with 6/3 with #?ground. Also can I just strip back the romex and feed it through the seal tite so I can just run it through the 4x4 wp j-box and the seal tite?? Thanks, JB


I believe most hot tubs require from the manufacture to be wired with #6 including the ground, as far as striping romex I believe that is not permitted because the individual wires in romex are not marked to identify what type of wire it is.
 
jute said:
...Also can I just strip back the romex and feed it through the seal tite so I can just run it through the 4x4 wp j-box and the seal tite?? Thanks, JB

Probably not. The whole romex cable is labeled as NM-B. If the individual conductors inside that cable are labeled as THWN or some other NEC wiring method you can push the individual conductors through, but I haven't seen any cable that has the individual wires labeled like that. One other problem with what you're proposing has to do with using romex outside. Take a look at 334.12(B)(4) and then look up the definition of damp and wet locations in article 100. 300.9 is the section that won't allow you to put the whole romex cable through the sealtite either.
 
jute said:
Can I fit 6/3 with ground in the existing 3/4" conduit. I used 8/3 with #10 ground and need to replace with 6/3 with #?ground.

The 3/4" thinwall is already installed from the panel down to the crawl space... Will 6/3 with ground fit through the 3/4" thinwall, lb, 4x4 sq wp j- box throught he seal tite?? also is the ground still #10??Thanks, JB
 
The Op does not say anything about the service disconnect either. Also the stripped NM would not have the insulated ground that is needed outside.

Instead of the WP box set the disco there and then make the transition.
 
jimport said:
The Op does not say anything about the service disconnect either. Also the stripped NM would not have the insulated ground that is needed outside.

Instead of the WP box set the disco there and then make the transition.

I thought I didn't need a disco because this is a single family dwelling, thas is also a prefabricated spa that has it's own GFCI and was told by Manuf I needed a 50a/220v/4wire cuircuit and hardwire it to the spa...
I'll use (3) #6 THWN (1) #10 (is #10 is the correct size?) except in the crawl space
and will this fit in 3/4"??
 
Last edited:
jute said:
I thought I didn't need a disco because this is a single family dwelling, thas is also a prefabricated spa that has it's own GFCI and was told by Manuf I needed a 50a/220v/4wire cuircuit and hardwire it to the spa...
I'll use (3) #6 THWN (1) #10 (I don't have my book, is #10 is the correct size?) EGC 250.122?, if so will this fit in 3/4" already installed??
Thanks to all for the help, JB

>>DUPLICATE MEANT TO EDIT PREVIOUS POST<<
 
Last edited:
jute said:
I thought I didn't need a disco because this is a single family dwelling, thas is also a prefabricated spa that has it's own GFCI and was told by Manuf I needed a 50a/220v/4wire cuircuit and hardwire it to the spa...
I'll use (3) #6 THWN (1) #10 (is #10 is the correct size?) except in the crawl space
and will this fit in 3/4"??

You don't need an emergency shut off. 680.41.
 
jute said:
I thought I didn't need a disco because this is a single family dwelling, thas is also a prefabricated spa that has it's own GFCI and was told by Manuf I needed a 50a/220v/4wire cuircuit and hardwire it to the spa...
I'll use (3) #6 THWN (1) #10 (is #10 is the correct size?) except in the crawl space
and will this fit in 3/4"??

You don't need an emergency shut off, but you do need a disconnect, they are not one in the same, also your feeder will need an insulated green ground wire.
 
You do not need an insulated ground wire n a dwelling if the wire is in the interior of the house. Once you get outside then you do. Art. 680.42(C) is very clear about this. Some Hot tub manufacturers are requiring a full sized ground. In that case nm cable will not work. You would be better off to pipe it from the 3/4 emt all the way to the outside if possible.

You cannot sleeve nm cable on the ext. of a house. Art. 334.12(B)(4) and art. 300.9 (2008 NEC)
 
Dennis Alwon said:
You do not need an insulated ground wire n a dwelling if the wire is in the interior of the house. Once you get outside then you do. Art. 680.42(C) is very clear about this. Some Hot tub manufacturers are requiring a full sized ground. In that case nm cable will not work. You would be better off to pipe it from the 3/4 emt all the way to the outside if possible.

You cannot sleeve nm cable on the ext. of a house. Art. 334.12(B)(4) and art. 300.9 (2008 NEC)
he never said he ran nm'b olong the outside of the house. I took it to mean he only used the nm'b to go throught the wall to the 4x4 j-box directly on the other side which would be fine
 
jute said:
I have a 50/50A 2 pole breaker installed in a 200a main panel... I used 3/4" thinwall conduit from the panel down to a 3/4" LB, I put a romex connector on the end of the LB and ran 50' of 8/3 with a #10 ground romex out to a 4x4 sq wp j-box mounted on the exterior of the house for an above ground spa hook up and from there I came out with a 6' whip of 3/4" seal tite to be hard wired to the spa. My question is can I fit 6/3 with ground in the existing 3/4" conduit. I used 8/3 with #10 ground and need to replace with 6/3 with #?ground. Also can I just strip back the romex and feed it through the seal tite so I can just run it through the 4x4 wp j-box and the seal tite?? Thanks, JB
#8 copper if using thwn is good enough for 50Amps
 
steelersman said:
he never said he ran nm'b olong the outside of the house. I took it to mean he only used the nm'b to go throught the wall to the 4x4 j-box directly on the other side which would be fine

Yeah, but he also said this

Also can I just strip back the romex and feed it through the seal tite so I can just run it through the 4x4 wp j-box and the seal tite

You can't do that either
 
Dennis Alwon said:
Yes in conduit but not as part of a NM cable.

I wanted to make sure this is right so I talked to the AHJ and told him I thought #8 was only good for 40A as per table 310.16 and I need a 50A 220v circuit. He told me the wire in FNMC (romex) was good becuase the wire can be based on the THWN 75* table which makes it good for 50A... He also told me to put a 60A knife disco instead of the 4x4 and from the disco to the spa use (3) #8 THWN and (1) #10 THWN in the seal tite...So after questioning him on the size and ampacity it looks like the wire is staying where it's at and I don't need to replace it with #6. Does this sound right doing like this?? Thanks again for all the help, JB
 
jute said:
I wanted to make sure this is right so I talked to the AHJ and told him I thought #8 was only good for 40A as per table 310.16 and I need a 50A 220v circuit. He told me the wire in FNMC (romex) was good becuase the wire can be based on the THWN 75* table which makes it good for 50A... He also told me to put a 60A knife disco instead of the 4x4 and from the disco to the spa use (3) #8 THWN and (1) #10 THWN in the seal tite...So after questioning him on the size and ampacity it looks like the wire is staying where it's at and I don't need to replace it with #6. Does this sound right doing like this?? Thanks again for all the help, JB

FNMC is not romex. Read art. 334.80
 
FNMC is flexible non metallic conduit and yes if you install thhn in it then it is good for 75C but NM is only good for 60C.
 
Dennis Alwon said:
FNMC is flexible non metallic conduit and yes if you install thhn in it then it is good for 75C but NM is only good for 60C.

Thanks, I'm not sure where I got that but I thought FNMC meant Flat Non Metalic Cable... My excuse is I'm usually on here early AM (4:24 am here) and not quite awake...I also need to get another NEC book whenever I'm on here it seems it's in the van...Thanks JB
 
Last edited: