Yes. I will pull a reduced neutral for a range or dryer when the wiring method is conduit - although I thought it wasn't technically allowed to reduce the neutral in a branch circuit?I noticed a 50 amp range cord package states it has 2-#6 and 2 -#8. I’m guessing the two #8 will be the neutral and the ground. Is this because the neutral will only carry the unbalanced load?
reality for most of them is a 14 AWG neutral would never be overloaded.The neutral load on a range is pretty low so it will never carry much current.
I have said this before, but this neutral thing drives me more and more crazy. I'd like to see the pile of copper wasted to supply oversized neutrals , or neutrals at all for that matter when a thing could easily be designed to not need it at all. My main client has a lot of 10 KW autoclaves, three phase 5 wire, neutral for the pilot lightreality for most of them is a 14 AWG neutral would never be overloaded.
If it weren't for 120 volt lamp in the oven maybe they would never even had a need for a neutral to begin with? They also used 120 volts for clocks and controls and often still do but certainly could have gone with 208-240 rated ones.
Where does it state that that is allowed? Never mind the range must be 83/4 kw or moreYes. I will pull a reduced neutral for a range or dryer when the wiring method is conduit - although I thought it wasn't technically allowed to reduce the neutral in a branch circuit?
That is a surprise to me. Do you know this for a fact?Some ranges use oven elements line-neutral during certain modes, so neutral current might be more substantial than nothing.
Some ranges use oven elements line-neutral during certain modes, so neutral current might be more substantial than nothing.
Yes, I think @Birken Vogt meant was the stove top eyes, not the oven heating elements. The eyes use a combination to regulate the heat.That is a surprise to me. Do you know this for a fact?
Right I am saying I think it is actually not allowed, but I do it anywayWhere does it state that that is allowed? Never mind the range must be 83/4 kw or more
Exception No. 2:
The neutral conductor of a 3-wire branch circuit supplying a household electric range, a wall-mounted oven, or a counter-mounted cooking unit shall be permitted to be smaller than the ungrounded conductors where the maximum demand of a range of 83⁄4 kW or more rating has been calculated according to Column C of Table 220.55, but such conductor shall have an ampacity of not less than 70 percent of the branch-circuit rating and shall not be smaller than 10 AWG.
I can't take you to a specific model, but we were having this argument for the umpteenth time 6 months to a year ago and somebody pointed out that oven elements of some models will use L-N for more consistent low heat sometimes. 1/2 the current 1/4 the power and all thatThat is a surprise to me. Do you know this for a fact?
I have wired some Wolfe stove that were straight 240Here’s the schematic on one, most of the newer ones probably use infinite electronic controls, and like new dryers, probably don’t even need a neutral anymore.