Marty Funkhauser
- The other side of aluminum
- electrical apprentice
Hello to everyone, newby here. 2.5yrs in. What are some typical uses for a single pole 50amp breakers @ 120volt?
Could be, its like clothes dryers, the drum motor is 120, but the heating elements are 208/240, where if the motor was 240, and used on say, an apartment building or condo that has three phase, 208 would be sufficient for the heating elements, but not the motor. Probably the same way with the warming drawers, 240 would be too hot with a 208 element, or a 240 volt element would not get hot enough on 208, so 120 volt elements would work on both systems.I’ve used them in commercial kitchens a handful of times in over 30 years... Mostly on warming or serving carts. Not sure why they provide them that way but possibly more compatible with voltages for single or three phase. Everything we order must be spec‘d 208V. since many pieces are available also in 240v. Maybe allows them to stock fewer versions???
(I've seen one or two where they don't belong.. eliminating pesky tripping on 20 amp circuits)
I see that a lot with Square D breakers, partly because they have low magnetic trip for 15 and 20 amp single pole standard breakers. DIY owner goes to big box or local hardware store and finds a single pole 30 and fixes their problem. Often is is the low magnetic trip function and a power tool that has high starting current and if one would install a 15 or 20 amp "high magnetic" breaker it will hold when starting that tool. But they don't generally have those at the big box or local hardware stores.I thought "proper procedure" for those occasionally tripping 20 amp circuits was a 30 not a 50!? I've got a single 70 laying around for those very troublesome circuits.
Yeah, had that problem last year with a hydraulic press, it worked fine on the other side of the shop, then they moved it over next to the service, and it would trip the breaker every time. Plugged it into a 100' extension cord, it worked fine. Customer wanted to change to a 30 amp breaker for the 20 amp receptacle. Refused, ordered a QOHM120, installed, no more problem.I see that a lot with Square D breakers, partly because they have low magnetic trip for 15 and 20 amp single pole standard breakers. DIY owner goes to big box or local hardware store and finds a single pole 30 and fixes their problem. Often is is the low magnetic trip function and a power tool that has high starting current and if one would install a 15 or 20 amp "high magnetic" breaker it will hold when starting that tool. But they don't generally have those at the big box or local hardware stores.
ADD: that low magnetic trip is IMO more effective at accomplishing many the goals that AFCI's have as well as doing it with less nuisance trips.
Whats the largest amp single pole breaker?I thought "proper procedure" for those occasionally tripping 20 amp circuits was a 30 not a 50!? I've got a single 70 laying around for those very troublesome circuits.
70Whats the largest amp single pole breaker?
I've seen 100, maybe even 200 in old farm meter main's, but they were basically unit breakers with lug on each end and not a plug on or bolt on breaker type. Many those old meter mains had two single pole and no common trip double pole breakers in them.Whats the largest amp single pole breaker?
Where does a 60 amp come into play with lighting circuits?I see high amp SP breakers in lighting panels. I had to replace a 60A in a Lutron panel. I had to order the breaker.
Probably stage lighting, multiple high wattage lamps.Where does a 60 amp come into play with lighting circuits?
50 amp lighting circuits once were more common then they probably are today. Code doesn't allow more than 50 amp for lighting branch circuits, but does have limitations on what kinds of lighting it can supply.