Will operating a 50hz transformer on a 60hz line cause a higher secondary voltage or is this just a myth? Or are any other issues probable?
The voltage is related to the turns ratio, not the frequency. So if you have a 240V to 24V transformer for example, the turns ratio is 10:1 so the output will still be 24V if the input is 240. The output will be at 60Hz of course.Will operating a 50hz transformer on a 60hz line cause a higher secondary voltage or is this just a myth? Or are any other issues probable?
The voltage is related to the turns ratio, not the frequency. So if you have a 240V to 24V transformer for example, the turns ratio is 10:1 so the output will still be 24V if the input is 240. The output will be at 60Hz of course.
The problem with different frequencies is in going from a 60Hz designed transformer and using it in a 50Hz supply. It still does not change the voltage, but the EFFECT of the lower frequency applied to the 60Hz designed transformer is said to be the same as applying over voltage to it; the transformer current is higher for a given load and because the transformer will not have been designed for that added I2t heating, it over heats and fails sooner. I only mention this because I have found that this is often the reason behind that myth / misunderstanding.
Is this a question based on curiosity of a real application?Will operating a 50hz transformer on a 60hz line cause a higher secondary voltage or is this just a myth? Or are any other issues probable?
Is this a question based on curiosity of a real application?
If it is for an actual application it would be appropriate to provide the rating of the transformer in question.
You could be referring to a CPT or a power transformer. Applying a transformer at a lower frequency than its rating will result in core saturation resultng heating which also affects the secondary voltage as the core saturates. This also happens with an overvoltage condition as was previously stated.
In either case 50hz rated transformers in general will function acceptably at 60hz as stated in previous posts. But, this would be a general answer and should not to be assumed to be true in every application.
Will operating a 50hz transformer on a 60hz line cause a higher secondary voltage or is this just a myth? Or are any other issues probable?
140827-0905 EDT
mbrooke:
How do you squeeze more kVA out of a transformer? Only if you were to raise the voltage.
To a large extent a transformer rating is current limited by I^2*R losses. Also note lower frequency transformers may use thicker laminations, and when run at higher frequencies will have higher eddy current losses.
.
IMHO... You would also have a change in the impedance value of the transformer.
I could be wrong: A 50hz transformer has more iron in it compared to a 60 cycle unit. My theory is there will be less saturation (assuming primary voltage stays the same), and in turn the unit will run slightly cooler, thus allowing for a slightly higher load until the same temperature rise is met.
Your onto something good.It would be lower, correct? Ie, a 5% Z 50hz would go to 4.5% Z 60hz?