ASCO gives instructions for using their ratings. I don't think the link will work: just search for "Asco Withstand Ratings":
Back to your application. The max. time to clear a fault is going to depend on the setting for the instantaneous, correct?
Highest setting gives a max. clearing time of about 0.025 seconds, which is more than one cycle. But at the minimum setting, it would clear in less than 0.001 seconds. It would be nice if they gave one more curve in between min and max.
If we assume the instantaneous is set to minimum, it looks like the breaker is OK. It will always trip in much less than a cycle.
If we look at the trip time for our maximum of 50K (83x600A), it is just slightly less than 17 ms. So it looks like we meet the 17ms withstand rating of 85K.
But now I'm confused. How do we know exactly what current to use to determine the maximum breaker opening time? Do we assume the maximum fault current available - 50KA for this example? I think that's how I've always done it.
But that doesn't seem quite fair, since the calculations are always conservative (the actual fault current will always be somewhat less), and the breaker will always take longer to open.