Here's 2 paragraphs, one is what's in the NEC, the other I made up all by my lonesome.
230.42(B)
(B) Specific Installations. In addition to the requirements of 230.42(A), the minimum ampacity for ungrounded conductors for specific installations shall not be less than the minimum rating of the service disconnecting means installed.
230.42(B)
(B) Specific Installations. In addition to the requirements of 230.42(A), the minimum ampacity for ungrounded conductors for specific installations shall not be less than the minimum rating of the service disconnecting means specified in 230.79(A) through (D).
Would the real 230.42(B) please stand up ?!
I don't see that the real 230.42(B) ever requires "minimum ampacity for ungrounded conductors" larger than 100a [230.79(C)].
Am I missing something ?
David