xguard
Senior Member
- Location
- Baton Rouge, LA
I have a 500 kva 3 phase transformer, 480:208/120. I know I can't use the "next size up rule" for the secondary conductors but can I for secondary protection? It looks like 240.4(B) is specifically about over current protection for conductors, not transformers.
(500,000/(sqrt3*208))*1.25 = 1,735 amps making the next standard size up 1,800 amps. I'm currently calling for one set of secondary conductors to a 1200 amp fused switch and another to a 600 amp fused switch. I'd like to keep it this way if I can.
Additional information:
1200 amp secondary conductors are 4-400 kcmil per phase
600 amp secondary conductors are 2-400 kcmil per phase.
(500,000/(sqrt3*208))*1.25 = 1,735 amps making the next standard size up 1,800 amps. I'm currently calling for one set of secondary conductors to a 1200 amp fused switch and another to a 600 amp fused switch. I'd like to keep it this way if I can.
Additional information:
1200 amp secondary conductors are 4-400 kcmil per phase
600 amp secondary conductors are 2-400 kcmil per phase.