electricaldoc
Member
We pulled wire for a 300 hp air compressor last night, and I ran into a couple of questions.
1 we used a 600A 480V 3phase breaker, but pulled only 500mcm THHN wire. Now this actually fed a disconnect that was to be fused at 400A. The problem I have is 500 THHN is not rated for 600A, and if 400 amp fuses were ever up sized to the full potential of 600A this would cause a problem.
Would this fall under 240.21(B)4 taps over 25ft? Or did we just make major code violation? An electrician on different shift made the call on wire size, and had already had 200ft of this wire shipped in for the job. Each leg had to be 60ft long so no way to parallel them plus when he quoted it boss told him we only need one set of 500. We had three men in there on double time to make pull before compressor would be set at 7:00am this morning. So no way to change mind then.
2 One of the electricians wanted to land the grounding conductor on a grounding box connector or bushing. This would have meant no grounding lug in disconnect, and when they landed the wires on load side the grounding conductor for load side would have also been connected to grounding bushing. I did not like this idea and since I made the land I added a grounding lug.
Now are both of these a code violation, or am I wrong?
1 we used a 600A 480V 3phase breaker, but pulled only 500mcm THHN wire. Now this actually fed a disconnect that was to be fused at 400A. The problem I have is 500 THHN is not rated for 600A, and if 400 amp fuses were ever up sized to the full potential of 600A this would cause a problem.
Would this fall under 240.21(B)4 taps over 25ft? Or did we just make major code violation? An electrician on different shift made the call on wire size, and had already had 200ft of this wire shipped in for the job. Each leg had to be 60ft long so no way to parallel them plus when he quoted it boss told him we only need one set of 500. We had three men in there on double time to make pull before compressor would be set at 7:00am this morning. So no way to change mind then.
2 One of the electricians wanted to land the grounding conductor on a grounding box connector or bushing. This would have meant no grounding lug in disconnect, and when they landed the wires on load side the grounding conductor for load side would have also been connected to grounding bushing. I did not like this idea and since I made the land I added a grounding lug.
Now are both of these a code violation, or am I wrong?