Re: 500KCMIL and 400A breaker
Let me expand on the question, for I had a similar discussion with my group last week. I will describe two installations. My question is this, ?Are the two installations different, in that a 400 amp breaker is permitted in the first, but not permitted in the second??
Installation #1: I want to serve an MLO sub-panel that have six disconnects serving downstream loads. I calculate the sub-panel?s total load (per NEC methods) to be 370 amps. I select a 500 MCM conductor (rated at 380 amps). I read 240.4(B) and conclude that a 400 amp breaker (i.e., the next higher standard size, but not over 800) is acceptable.
Installation #2: I install a 400 amp breaker panel. I select a 500 MCM conductor (rated at 380 amps). I read 240.4(B) and conclude that a 400 amp breaker (i.e., the next higher standard size, but not over 800) is acceptable.
Why might the two be different? Because in Installation #1, I know that the load is less than the ampacity of the 500 MCM feeder, and I know that no more disconnects can be installed. However, in Installation #2, someone could come behind me and load up that 400 amp panel to more than 380 amps.
In other words, if I know that the load can exceed the ampacity of the cable, can I still use that cable? I am considering ?load? versus ?cable ampacity,? rather than 240.4(B)?s ?cable ampacity? versus ?cable protection.?