Will the code authorities allow "use of 400 Amp breaker, with a 500KCMIL cable", which is suitable for only 380 Amps (75 deg. rating)?

Any ideas !!!!
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: 500KCMIL and 400A breaker

In many cases, 240.4(B) will permit you to use the 500 kcmil on the 400 amp breaker.
Don
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Semi-Retired Electrical Engineer
Re: 500KCMIL and 400A breaker

Let me expand on the question, for I had a similar discussion with my group last week. I will describe two installations. My question is this, ?Are the two installations different, in that a 400 amp breaker is permitted in the first, but not permitted in the second??

Installation #1: I want to serve an MLO sub-panel that have six disconnects serving downstream loads. I calculate the sub-panel?s total load (per NEC methods) to be 370 amps. I select a 500 MCM conductor (rated at 380 amps). I read 240.4(B) and conclude that a 400 amp breaker (i.e., the next higher standard size, but not over 800) is acceptable.

Installation #2: I install a 400 amp breaker panel. I select a 500 MCM conductor (rated at 380 amps). I read 240.4(B) and conclude that a 400 amp breaker (i.e., the next higher standard size, but not over 800) is acceptable.

Why might the two be different? Because in Installation #1, I know that the load is less than the ampacity of the 500 MCM feeder, and I know that no more disconnects can be installed. However, in Installation #2, someone could come behind me and load up that 400 amp panel to more than 380 amps.

In other words, if I know that the load can exceed the ampacity of the cable, can I still use that cable? I am considering ?load? versus ?cable ampacity,? rather than 240.4(B)?s ?cable ampacity? versus ?cable protection.?
 

sjaniga

Member
Re: 500KCMIL and 400A breaker

Charlie,
In your first installation, would'nt the 380 amp load on a 400 amp breaker be too much, and shouldnt you install a 600 amp. just a thought.
 

gwz2

Senior Member
Location
Indiana
Re: 500KCMIL and 400A breaker

Many MLO panelboards used as Service Equipment can accept more than 6 OCPD.

I really don't see any real difference between #1 and #2 except the anticipated load is calculated in #1.

Thus acceptable.
 

BAHTAH

Senior Member
Location
United States
Re: 500KCMIL and 400A breaker

Unless the breaker is 100% rated, the maximum load you can apply continuously is 320amps. The NEC requires the feeder conductors to have a minimum ampacity of not less than the noncontinuous load plus 125% of the continuous load. The NEC also required the overcurrent protection for a feeder to have a load rating not less than the noncontinuous load plus 125% of the continuous load. 500KCM CU is good for 380 amps, 240.4(B) would allow the 400amp breaker to protect the 500KCM, however since the breaker should not see anything over 320amps continuous there should be no problem. If you know the load will exceed the design of 320amps then you would need to design the feeder based on the higher load. Even if the load went to 400amps for a short time, the conductor insulation is designed for 430amps (THHN), so the breaker trips and you have an underdesigned system but no insulation failure.
 

definitive

Member
Location
Washington
Re: 500KCMIL and 400A breaker

Ok maybe this is a stretch, but it seems to me that #1 is a branch circuit panel, and #2 is a main service. Is this the case?
 