Art 501.10(A)(3) states "All boxes and fittings shall be approved for Class I, Division 1"
To me, this means Nema 7 construction or equivalent.
Art 501.15(A)(1) Exception states basically conduit seals shall not be required entering enclosures where the switch, CB, fuse etc, is enclosed within a factory sealed explosionproof chamber located within the enclosure.
Therefore as long as the enclosure is explosionproof (e.g. Nema 7) in this case, a start-stop pushbutton control station, and contains has a factory sealed contact block, a conduit seal is NOT required.
Please confirm.