To use the exception to 501.105(B)(3) the NFPA 2017 says "...and if the marked maximum operating temperature any exposed surface will not exceed 80 percent of the AIT in degrees C..." What is meant by "MARKED" here. If the general purpose enclosure in question is a single component of a larger piece of Machinery, would the OEM of the larger piece of Machinery be able to test and mark the surface temperature of the component even though they are not the manufacturer of the individual component?
The item in question is a pneumatic solenoid bank that has built in Ethernet. The Solenoid bank itself is explicitly allowed per 501.105(B)(4), but the electronics involved with the ethernet portion lead me to 501.105(B)(3). The AIT is 400 C, so the equipment OBVIOUSLY does not get anywhere near the AIT. The hazardous area is Class I Div 2. To properly use the bank, can I test the exposed surfaces and see then mark the enclosure with this temperature? Is there anyway to use 500.8(C)(5) Special Allowances for General Purpose equipment as reasoning not have to mark the component?