We have a situation where EMT (20' segment) passes completely through a Class 1, Div 2 area without any couplings, boxes or fittings within 12" of each boundary. 501.15(B)(2) Exception No. 1: states that "Metal conduit that contains no unions, couplings, boxes, or fittings, and passes completely through a Class I, Division 2 location with no fittings less than 300 mm (12 in.) beyond each boundary, shall not require a conduit seal if the termination points of the unbroken conduit are in unclassified locations."
Since EMT is steel (metal), this would appear to be acceptable, but I'm not sure if they are implying rigid metal conduit. 358.18(4) EMT Uses not permitted, states "not in any hazardous location except as permitted by other articles of this Code." This is vague and doesn't help.
Any comments or experience??