Sorry, I was just yanking your chain. Attached is the Proposal that got this problem started in the 2005 NEC. Note Donnie Cook, the Chairman of CMP14 at the time, was concerned that there was no identification of a suitable sealing method.
2005 ROP P14-34.pdf
To this day, his concerns have not been addressed directly by CMP14 or any NRTL.
My concern is that, while I agree that most Division 2/Unclassified seals are unnecessary - some still are. Usually, for Division 2, there should be no gases to migrate in the first place.
The problem is, if preventing the migration of gases is the actual purpose, then, unlike the Section 504.70 cited for intrinsically safe systems, those gases (if present) still could be ignited by Division 2 wiring methods. SO - if seal is needed at all, it should be
explosionproof.
It would have been better to have stated no boundary seals were needed except in a few cases. Two examples:
- Where grade is the boundary and the gases/vapors involved are heavier than air.
- Where there is a reasonable expectation that the Division 2 location has a positive pressure with respect to the Unclassified location AND there is reason to believe the gases would collect in the unclassified location.
In either case the seal should be
explosionproof.
BTW the same problem actually exists in Section 504.70 since circulating ground currents could still ignite the subject gases. (Hence the emphasis of Sections 504.50 and 60)