Natfuelbilll
501.15(B)(2) Exception No. 4
Exception No. 4: Segments of aboveground conduit systems shall
not be required to be sealed where passing from a Division 2
location into an unclassified location if all of the following conditions
are met:
(1) No part of the conduit system segment passes through a
Division 1 location where the conduit segment contains unions,
couplings, boxes, or fittings that are located within 300 mm (12
in.) of the Division 1 location.
(2) The conduit system segment is located entirely in outdoor
locations.
(3) The conduit system segment is not directly connected to canned
pumps, process or service connections for flow, pressure, or
analysis measurement, and so forth, that depend on a single
compression seal, diaphragm, or tube to prevent flammable or
combustible fluids from entering the conduit system.
(4) The conduit system segment contains only threaded metal
conduit, unions, couplings, conduit bodies, and fittings in the
unclassified location.
(5) The conduit system segment is sealed at its entry to each
enclosure or fitting located in the Division 2 location that
contains terminals, splices, or taps.
Soooo....
1. An aboveground conduit leaving an C1D2 location and ran underground (an unclassified location) will not need a boundary seal if (1) through (5) are satisfied?
2. An aboveground conduit leaving an C1D2 location and ran aboveground (to an unclassified location) will not need a boundary seal if (1) through (5) are satisfied?
3. What exactly is the difference between a conduit run and a conduit system segment?
4. How does not installing a seal, as allowed per this exception, fulfill the purpose minimizing the passage of gases being accomplished with a boundary seal?
Thank you in advance for your responses.
are met:
locations.
Soooo....