Natfuelbilll
Senior Member
This section of the Code is confusing, or, I am a blockhead.
The area is C1D2.
Question 1
"The sealing fitting shall comply with 501.15(B)(I). Multiconductor cables with a gas/vaportight continuous sheath capable of transmitting gases or vapors through the cable core shall be sealed in a listed fitting in the Division 2 location after removing the jacket and any other coverings."
Is the "shall be sealed in a listed fitting" phrase requiring the fitting to be only a conduit seal fitting, or is there some other type of cable fitting?
Question 2
Could one re-write the last sentence of 501.15(E)(1) "Multiconductor cables in conduit shall be sealed as described in 501.15(D)." as "Multiconductor cables in conduit , where the conduit enters an enclosure required to be explosionproof, shall be sealed as described in 501.15(D)." and be correct?
Question 3
For conduit equal or greater than 2" used in C1D2 to an enclosure that is not required to be explosionproof. Is there any scenario (non-boundary and non-ignition source) where the Code requires a seal because of the large 2" size and terminals, splices, or taps? ala 501.15(A)(1)(2) ?
The area is C1D2.
Question 1
"The sealing fitting shall comply with 501.15(B)(I). Multiconductor cables with a gas/vaportight continuous sheath capable of transmitting gases or vapors through the cable core shall be sealed in a listed fitting in the Division 2 location after removing the jacket and any other coverings."
Is the "shall be sealed in a listed fitting" phrase requiring the fitting to be only a conduit seal fitting, or is there some other type of cable fitting?
Question 2
Could one re-write the last sentence of 501.15(E)(1) "Multiconductor cables in conduit shall be sealed as described in 501.15(D)." as "Multiconductor cables in conduit , where the conduit enters an enclosure required to be explosionproof, shall be sealed as described in 501.15(D)." and be correct?
Question 3
For conduit equal or greater than 2" used in C1D2 to an enclosure that is not required to be explosionproof. Is there any scenario (non-boundary and non-ignition source) where the Code requires a seal because of the large 2" size and terminals, splices, or taps? ala 501.15(A)(1)(2) ?