eric

Member
Location
Kansas
would like to have a explanation of this code article. we have a storage shed with a panel inside from this panel i have refed an existing above ground gas tank used to refuel equipment. pvc underground change to rigid sealoff atfirst joint out of ground. inspector says i also must follow 501-16a is this required when equipment grnd is installed in this branch circut
 
Re: 501-16a

Please forgive me, but I've read this post about a half-dozen times and I still don't know what you are asking.

At the moment, the best I can do is say you must indeed comply with 501.16(A) in Class I locations; but I'm not sure why the inspector might say you haven't. Sec 501.16(A) has several requirements and simply running a separate EGC by itself won't necessarily be automatically compliant. Its certainly a good start.
 
Re: 501-16a

If you ran rigid from the seal off fitting EYS to the panel and the dispensig unit you would probably need an insulated ground bushing with a ground attached to satisfy your inspector.
 