thenols
New User
- Location
- Washington State
- Occupation
- Engineer
This is a new area of the code to me, so I'm trying to figure out if I'm applying this correctly.
I am working on a project where an instrument, in this case a pressure transmitter, is installed in a pipe. The inside of the pipe has been designated a Class I, Div 1, Group B location, but the air space that the instrument is in has been designated as unclassified. The instrument has a number of ratings, including IS, for Cl.I Div.1, NI for Cl.I Div.2, and DIP for Cl.II, Div 1. It is also marked and rated as FM Approved "Single Seal."
The manufacturer on the control drawing lists pressure and temperature requirements to be "Single Seal" rated, which we follow. If it is in fact FM Approved Single Seal, and the only classified environment is inside the piping, do I need to apply protection techniques (like Explosionproof equipment, Intrinsic safety, or others), or is meeting the Single Seal requirement sufficient to protect against the explosion hazard?
I am working on a project where an instrument, in this case a pressure transmitter, is installed in a pipe. The inside of the pipe has been designated a Class I, Div 1, Group B location, but the air space that the instrument is in has been designated as unclassified. The instrument has a number of ratings, including IS, for Cl.I Div.1, NI for Cl.I Div.2, and DIP for Cl.II, Div 1. It is also marked and rated as FM Approved "Single Seal."
The manufacturer on the control drawing lists pressure and temperature requirements to be "Single Seal" rated, which we follow. If it is in fact FM Approved Single Seal, and the only classified environment is inside the piping, do I need to apply protection techniques (like Explosionproof equipment, Intrinsic safety, or others), or is meeting the Single Seal requirement sufficient to protect against the explosion hazard?