If there is a pressure switch that meets the 504.2 definition of simple apparatus, and is connected to an Intrinsically Safe Isolator, does 501.17 apply in any way to this pressure switch.
501.17 says "Process-connected electrical equipment that does not rely on a single process seal or is lested and marked "single seal" or "dual seal"" shall not be re required to be provided with an additional means of sealing..."
Since the intrinsic isolator is used, then the process seal is not relied upon for protection. Or, would the intrinsic isolator and an extra means of process sealing need to be used per 501.17.
It is a Class I Division 2 location...
501.17 says "Process-connected electrical equipment that does not rely on a single process seal or is lested and marked "single seal" or "dual seal"" shall not be re required to be provided with an additional means of sealing..."
Since the intrinsic isolator is used, then the process seal is not relied upon for protection. Or, would the intrinsic isolator and an extra means of process sealing need to be used per 501.17.
It is a Class I Division 2 location...