501.30 grounding and bonding

Status
Not open for further replies.

Dsg319

Senior Member
Location
West Virginia
Occupation
Wv Master “lectrician”
Most natural gas facilities I tend to work at we always use the bonding style Myers hub with a bonding screw.1FFF5C36-F962-4624-8967-81A018AD58A7.jpeg

It says bonding jumpers with proper fittings and other approved means of bonding shall be used

Can I get some examples of other approved bonding means other than the typical red myer hub with the bonding screw.
 
See Section 250.100. There is a nest of circular cross-references, but the key is that locknut-bushing and double-locknut are NOT acceptable among the more commonly accepted methods in general use. Remember this applies to both Divisions 1 and 2. Most (not all) ordinary location methods are acceptable in Division 2.
 