501.30 grounding and bonding

Status
Not open for further replies.

Dsg319

Senior Member
Location
West Virginia
Occupation
Wv Master “lectrician”
Most natural gas facilities I tend to work at we always use the bonding style Myers hub with a bonding screw. 1FFF5C36-F962-4624-8967-81A018AD58A7.jpeg

It says bonding jumpers with proper fittings and other approved means of bonding shall be used

Can I get some examples of other approved bonding means other than the typical red myer hub with the bonding screw.
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
See Section 250.100. There is a nest of circular cross-references, but the key is that locknut-bushing and double-locknut are NOT acceptable among the more commonly accepted methods in general use. Remember this applies to both Divisions 1 and 2. Most (not all) ordinary location methods are acceptable in Division 2.
 