501.40 ('08) states that a MWBC can not be used in C1D1 location, but than gives the exception (...exception: all ungrounded conductors must simultaneously open) The exception in 501.40 basically is the requirement for MWBC in 210.4(B) (states that MWBC must be simultaneously disconnected).
My question is why state that it can not be used when applied in 501.40, when 210.4(B) must be satisfied regardless to the location?