502.10 (a)(2)

Status
Not open for further replies.

Matt Rider

New member
In 502.10 (A)(2)(2) Liquidtight flexable metal conduit with listed fittings.
Does the word listed fittings mean listed for use with liquidtight flexable metal conduit or listed for use in a class 2 division 1 location.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Listed for use with the lquidtight flexible metal conduit. This section isn't really needed any more because a couple of code cycles ago they added 350.6 which also requires the use of listed fittings.
Don
 