50A Portable Generator inlet Box Feeder Wire size

wmeek

Senior Member
Location
Texas
Occupation
Electrician
I am installing a 50A Generator Inlet box with a 2p50 in Main panel with mechanical Interlock. My Question is if I use romex wiring i would be required to use 6/3 with ground. If I was to install this Feeder in Emt Conduit , I can use #8 Thhn and a #10Thhn.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Thank you for the clarification
You're welcome, the use of #8 is contingent upon the inlet having 75° C connections. Some do not. I had to use an inlet with factory pigtails to utilize the 75°C conductor rating.
 