Instructions for a kiln quote load at 48A. Comes with 6-50P (50A plug). Requires 60A Fuse. As far as I can see, this violates 210.21(B)(1). I e-mailed the manufacturer and this is what I got back:
"The use of a 50 amp plug on kilns with a 60 amp circuit is a widespread and long standing practice that has been approved by UL."
What am I missing? I'm guessing that UL approved a 50A plug on a 48A load by assuming is was NOT continuous, but that's just a guess. Anyone else run into this? I just don't get how I can put a 50A receptacle on a 60A circuit and meet the code requirements.
Thanks and Happy Holidays,
Mark
"The use of a 50 amp plug on kilns with a 60 amp circuit is a widespread and long standing practice that has been approved by UL."
What am I missing? I'm guessing that UL approved a 50A plug on a 48A load by assuming is was NOT continuous, but that's just a guess. Anyone else run into this? I just don't get how I can put a 50A receptacle on a 60A circuit and meet the code requirements.