50amp cord into 30 amp campground service

Status
Not open for further replies.

muskiedog

Senior Member
Location
Minnesota
I am trying to find some warning signage on doing this practice at our county parks. Campers will plug in a 50amp with a cheater cord and then start turning stuff off till the stop tripping the 30 amp breaker. Is there code against this practice?
 

paul

Senior Member
Location
Snohomish, WA
Re: 50amp cord into 30 amp campground service

No there is no code against it, because everything down line from the 30 amp breaker will handle 30 amps without an overheating problem. That 'cheater' cord you mention is actually U.L. listed. They also make one so that you can plug your 30 amp camper into a 50 amp recept. That is against code because your 30 amp camper and wiring can theoretically take up to 50 amps without tripping. The #10 wire and insulation doesn't like that and the adapters are not U.L. listed.
 

muskiedog

Senior Member
Location
Minnesota
Re: 50amp cord into 30 amp campground service

Thats what I thought, I had seen in the code 551.71 that we should just ensure that we have both in place to eliminate this practice.

thanks
 