I have a 50HP ABB drive and 75HP pump which I'd like to pair up on a temporary basis. Vendor is telling me that there is no reason why it wouldn't work; the obvious draw back being that you won't get the full capacity of the pump but that it is a code violation.
Is it? and if so, why is it. If you can set the electronic overload appropriately, why would this be in any way unsafe?
Thanks,
Mike
Code violation possibility: 110.3... Suitability for installation and use... The VFD is listed and labeled for a maximum 30HP motor, you are not using it for a 30HP motor, you are using it for a 50HP motor, ergo it is not "suitable".
BUT... you CAN set up the drive to "current limit" at the
maximum rating of the DRIVE so that it never is allowed to deliver more than the current normally associated with 30HP to the motor. So you COULD make an argument that you are NOT in fact using it beyond its listed purpose. Whether or not an AHJ will buy that argument is basically a craps shoot...
On that note, I have done it many times very successfully, with the limitations as you described. The usual situation is that, to use you your example, I had a 30HP motor and VFD on something like a pump and the motor failed. The only available motor for a few weeks was a 50HP. Install and adapt the 50HP motor, program the VFD to never exceed 30HP, but I already knew that 30HP was sufficient because the 30HP motor had worked. It does cost you in efficiency, so you will want to put in the right motor again as soon as possible.