For a 50MVA (138/69/13.8 KV) Transformer, what would be the maximum demand in order not to exceed 80% of its operating capacity.
ANSI Stansard C57.92 tells you everything you want to know about loading Oil immersed transformers.For a 50MVA (138/69/13.8 KV) Transformer, what would be the maximum demand in order not to exceed 80% of its operating capacity.
The simple answer is 50 x .80 = 40.
Though, I assume there is a lot more behind your question.
What do you mean by 'demand'?
How does that relate to your limit of 80%
Why are you concerned with only loading it 80%?
I mean Demand in MW or the equivalent MW to load the transformer @80% of its capacity.
50 MVA and 50MW are not the same thing.
A transformer can be loaded to it's full nameplate rating.
A transformer with these voltages sounds like a 3-winding substation transformer (138/69/13.8 KV).
Why are you concerned with only loading it 80%?