D davidaengelhart Member Location Collier County (Naples), Florida, USA Sep 24, 2008 #1 Is the E-stop button, that is located within 100 feet of the fuel pumps and near the attendant, to disconnect the grounded neutral conductor (if applicable) as well as the ungrounded circuit conductors?
Is the E-stop button, that is located within 100 feet of the fuel pumps and near the attendant, to disconnect the grounded neutral conductor (if applicable) as well as the ungrounded circuit conductors?
rbalex Moderator Staff member Location Mission Viejo, CA Occupation Professional Electrical Engineer Sep 24, 2008 #2 Yes. See the last sentence of the first paragraph of Section 514.11(A)