chevyx92
Senior Member
- Location
- VA BCH, VA
514.16 said all metal raceways need to be grounded and bonded and shall comply with 501.30.
501.30(B)(1) the locknut-bushing and double locknut types of contacts shall not be depended on for bonding purposes, but bonding jumpers with identified fittings or other approved means of bonding shall be used. My question is, can I use bonding locknuts to establish bond for conduit? Or do I have to use grounding bushings? This installation will have EMT installed inside, so I would like to use bonding locknuts at junction boxes and not grounding bushings if possible to comply with 514.16.
501.30(B)(1) the locknut-bushing and double locknut types of contacts shall not be depended on for bonding purposes, but bonding jumpers with identified fittings or other approved means of bonding shall be used. My question is, can I use bonding locknuts to establish bond for conduit? Or do I have to use grounding bushings? This installation will have EMT installed inside, so I would like to use bonding locknuts at junction boxes and not grounding bushings if possible to comply with 514.16.