Im having trouble with 514. SO I have a few questions
1. 514 .9 The article mentions each conduit leaving or entering a fuel dispenser must have seal off. I have dispenser and it happens to feed a sign that sits 2' away on same fuel island. does the sign also need to have a seal off going into sign? The sign is inside the boundry so I assume it does.
2. if the canopy lighting and speakers conduit also runs inside boundry but energe above the 18' boudry to the top of canopy, would I need a seal off at canopy also?
3. I tried searching but cant locate where if mentions that I need a seal off as conduit leaves the C store and 1 at dispeners. Dispenser is 501.15 4 but the C store I cant locate.
 
Nothing in 514 changes the sealing requirements in 501.15. Conduits crossing a classification boundary require seals, but there are some exceptions in 501.15(B) for Division 2 boundaries.
 