I have encountered an interesting situation. One jurisdiction where I am employeed accepts a letter from a registered engineer to be accepted in leiu of a UL or NRTL listing.
A plant in that area installed a paint spray room aong with a mix room and other equipment, some of which had no listing or labeling. An engineer was hired and asked to "certify" the equipment and to classify the Hazardous area. There are electrical components installed on the outside of the booth
within inches of a roll- up door. These cocponents are in a NEMA 1 enclosure.
The engineer says "no problem, since there is a door".
Not that it matters since the AHJ accepts his letter as final word, but is my thinking correct that the engineer is (gawd forbid) wrong based on:
From 2005 NEC"
"516.3 Classification of Locations:
(C) Class I or Class II, Division 2 Locations The following spaces shall be considered Class I, Division 2 or Class I, Zone 2, or Class II, Division 2 as applicable.
(4) Enclosed Booths and Rooms For spraying operations confined to an enclosed spray booth or room, the space within 900 mm (3 ft) in all directions from any openings shall be considered Class I, Division 2, Class I, or Zone 2, or Class II, Division 2 as shown in Figure 516.3(B)(4). [NFPA 33:6.5.4]"
A plant in that area installed a paint spray room aong with a mix room and other equipment, some of which had no listing or labeling. An engineer was hired and asked to "certify" the equipment and to classify the Hazardous area. There are electrical components installed on the outside of the booth
within inches of a roll- up door. These cocponents are in a NEMA 1 enclosure.
The engineer says "no problem, since there is a door".
Not that it matters since the AHJ accepts his letter as final word, but is my thinking correct that the engineer is (gawd forbid) wrong based on:
From 2005 NEC"
"516.3 Classification of Locations:
(C) Class I or Class II, Division 2 Locations The following spaces shall be considered Class I, Division 2 or Class I, Zone 2, or Class II, Division 2 as applicable.
(4) Enclosed Booths and Rooms For spraying operations confined to an enclosed spray booth or room, the space within 900 mm (3 ft) in all directions from any openings shall be considered Class I, Division 2, Class I, or Zone 2, or Class II, Division 2 as shown in Figure 516.3(B)(4). [NFPA 33:6.5.4]"