So I have a question about the requirements of 517.13(A). Yes, I read it. Yes, I own the Mike Holt illustrated guide to 500-820 and read that.
Now, I understand that all wiring in or serving patient care areas must comply with 517.13(A). But what I have a question about is this, someone is telling me that I cannot change from HFC to MC between the patient care area and the panel. For instance, I would think it would be fine to run regular mc from a panel to a box in a nearby space that is not designated as a patient care space and then break out of that box with HFC to actually serve the patient care areas. I really don't see how this is a problem. They are telling me that I have to run HFC all the way back to the panel. To me, this just doesn't make sense because that redundant ground that is the jacket, is terminating inside a connector in a box that will be grounded to the insulated grounding conductor and will be a better ground to the panel than the jacket ground having to go through snap in connectors.
I am having a really hard time believing that the intent of the redundant ground is to actually increase the fault current capability of the circuit as this person is alleging. I think it more likely that in the unlikely case a wall and the mc inside it become damaged and accessible, the intent is to ensure that if the hot shorts to the jacket, it will ground out and trip the breaker or at the very least, keep the jacket from becoming a hot conductor. Both of which would still be the case if I switch to regular mc outside of the patient care area.
Now, I understand that all wiring in or serving patient care areas must comply with 517.13(A). But what I have a question about is this, someone is telling me that I cannot change from HFC to MC between the patient care area and the panel. For instance, I would think it would be fine to run regular mc from a panel to a box in a nearby space that is not designated as a patient care space and then break out of that box with HFC to actually serve the patient care areas. I really don't see how this is a problem. They are telling me that I have to run HFC all the way back to the panel. To me, this just doesn't make sense because that redundant ground that is the jacket, is terminating inside a connector in a box that will be grounded to the insulated grounding conductor and will be a better ground to the panel than the jacket ground having to go through snap in connectors.
I am having a really hard time believing that the intent of the redundant ground is to actually increase the fault current capability of the circuit as this person is alleging. I think it more likely that in the unlikely case a wall and the mc inside it become damaged and accessible, the intent is to ensure that if the hot shorts to the jacket, it will ground out and trip the breaker or at the very least, keep the jacket from becoming a hot conductor. Both of which would still be the case if I switch to regular mc outside of the patient care area.