Is clear the two conditions in 517.13 that in Patient Cares Spaces, including OR, the use of wiring method shall be qualify as equipment grounding conductor and beside that every circuit from the isolated panel shall be run with green wire type equipment grounding conductor which is connected to grounding terminals of receptacles, metal boxes, device boxes.
The fact is the PM assistant was doing grounding test and mandate to disconnect the ground pigtail saying that specifically in OR is no allow to bond the metal box with the equipment grounding conductor running with the circuits originated in the Iso Panel.
I believe he's wrong and violate 517.13b.
My question is why to bond the metal boxes to provide an effective ground fault current path if there's no neutral in the Isolate power system and is not allow the operation of overcurrent device.
Any input and clarification is appreciated.
Thanks in advance
The fact is the PM assistant was doing grounding test and mandate to disconnect the ground pigtail saying that specifically in OR is no allow to bond the metal box with the equipment grounding conductor running with the circuits originated in the Iso Panel.
I believe he's wrong and violate 517.13b.
My question is why to bond the metal boxes to provide an effective ground fault current path if there's no neutral in the Isolate power system and is not allow the operation of overcurrent device.
Any input and clarification is appreciated.
Thanks in advance