The performance of the grounding system is made effective through the existence of the green grounding wire, the metal raceway, and all of the other building metal. Measurements have shown that it is the metal raceway and building steel that provide most of the effective grounding path of less than 10 milliohms at the receptacle, including plug to receptacle impedance. The green grounding wire becomes a backup, not a primary path performer.
So as long as you use EMT conduit and run an EGC within it (and they are tied together at each end of the conduit), you meet the intent of this code?
I guess I am trying to figure out how this is any different than what we normally do. We (firm I work in) typically only allows EMT in the interior with flex for special uses only... very rare for nonmetallics except for service entrance type conduits. We also always call out for a separate green grounding conductor.
So as long as you use EMT conduit and run an EGC within it (and they are tied together at each end of the conduit), you meet the intent of this code?
I guess I am trying to figure out how this is any different than what we normally do. We (firm I work in) typically only allows EMT in the interior with flex for special uses only... very rare for nonmetallics except for service entrance type conduits. We also always call out for a separate green grounding conductor.