chris kennedy
Senior Member
- Location
- Miami Fla.
- Occupation
- 60 yr old tool twisting electrician
I have a new EE that has speced IG recepticals for patient care areas. My first thought was you can't do that, it's a voilation of 517.13.
Then I looked around and found this.
Then I looked around and found this.
So I'm a little confused as to how using an IG rec doesn't violate 517.13.517.10 Applicability.
(A) Applicability. Part II shall apply to patient care areas of all health care facilities.
517.16 Receptacles with Insulated Grounding Terminals.
Receptacles with insulated grounding terminals, as permitted in 250.146(D), shall be identified; such identification shall be visible after installation.
FPN: Caution is important in specifying such a system with receptacles having insulated grounding terminals, since the grounding impedance is controlled only by the equipment grounding conductors and does not benefit functionally from any parallel grounding paths. This type of installation is typically used where a reduction of electrical noise (electromagnetic interference) is necessary and parallel grounding paths are to be avoided.