517.13

Status
Not open for further replies.

MEP

Member
NEC 517.13 specifies HCF-90 in a hospital.

My electrical contractor used Super Neutral Cable in lieu of HCF(for homeruns)

The hospital is questioning this practice.

The contractor says this is within NEC code.

Any help in this matter would be greatly appreciated
 
Re: 517.13

Super neutral is type MC cable and is not a substitute for HCFC which provide redundant equipment grounding conductors.
 
Re: 517.13

I agree with Infinity, Super Neutral MC will not provide the redundant grounding provided by HCFC.

There is a hospital grade MC on the market now, but it will have a runner inside the sheath the same as HCFC does.

As an aside, there may be another problem if any of these home runs are from the Critical or Life Safety Branches, flexible cables are only permitted in specific cases, and overall circuitry is not one of them.

See note # 3 below, and notice overall branch circuit wiring is not included.


517.30(C)(3)
Mechanical Protection of the Emergency System

The wiring of the emergency system in hospitals shall be mechanically protected. Where installed as branch circuits in patient care areas, the installation shall comply with the requirements of 517.13(A) and 517.13(B). The following wiring methods shall be permitted:
(1) Nonflexible metal raceways, Type MI cable, or Schedule 80 rigid nonmetallic conduit. Nonmetallic raceways shall not be used for branch circuits that supply patient care areas.

(2) Where encased in not less than 50 mm (2 in.) of concrete, Schedule 40 rigid nonmetallic conduit, flexible nonmetallic or jacketed metallic raceways, or jacketed metallic cable assemblies listed for installation in concrete. Nonmetallic raceways shall not be used for branch circuits that supply patient care areas.

(3) Listed flexible metal raceways and listed metal sheathed cable assemblies in any of the following:
a. Where used in listed prefabricated medical headwalls
b. In listed office furnishings
c. Where fished into existing walls or ceilings, not otherwise accessible and not subject to physical damage
d. Where necessary for flexible connection to equipment


(4) Flexible power cords of appliances or other utilization equipment connected to the emergency system.

(5) Secondary circuits of Class 2 or Class 3 communication or signaling systems
Roger
 
Re: 517.13

The Super Neutral Cable is used for home runs (normal power only) on Patient floors, doe this affect your response at all?

The Contractor has also suggested installing a ground buss at every Normal Panel connecting all of the MC jackets directly to the ground buss in the panel. And at the junction box at the end of each homerun the metal jacket be connected with a through bolt to the redundant ground within the box insuring that there is redundant grounding( the 2 green wires) and conductivity of the metal jacket just in case for some unlikely reason that the armor should be separated. Does this offer an acceptable solution per the electrical code and Hospital regulations?

{Moderator's Note: Edited to remove a request for assistance outside the scope of the Forum.}

[ November 01, 2005, 12:01 PM: Message edited by: charlie b ]
 
Re: 517.13

Installing a "ground bus" in the panel will not make the sheath of standard or Super Neutral MC an Equipment Grounding Conductor as recognized in 250.118.

Read the links below.

http://www.healthcareengineering.net/archive/receptacle/Article_from_RTT99_Launch.pdf specifically Reference Grounding Point

and

http://www.afcweb.com/prod-cat.htm

notice in this link the "Reference and Ratings" of each type of cable, you will see that compliance with 517 is not included in the MC information.

Roger

[ November 01, 2005, 10:27 AM: Message edited by: roger ]
 
Re: 517.13

I agree with Roger. I notice you mentioned "2 green wires". I've heard that this was once proposed to the NEC, and rejected by the NEC, as an alternate method of ensuring a ground connection.

The ground aside, I can't believe the contractor used flexible MC cable for the homeruns. I would have guessed there would have been project specifications that prevented this. I wouldn't ever allow a contractor to use MC or AC cable for home runs in a hospital. I would always specify wire in metal conduit.

One other note, MC cable must be supported and secured every 6'. Did the contractor do that?

Steve
 