517.30.C.3(1) Mechanical protection for Em ckts

Status
Not open for further replies.

BAMiller2408

Member
Location
CA
A co-worker and I have looked at this extensively and have come to the conclusion that HCF90 mc cable can be used for the Emergency circuit in a Nursing home. 517.30.C.3(1) applys to hospitals only.

Any comments?

 
Nothing prevents you from apply 517.30.C.3(1) for nursing home;) jk
 
A co-worker and I have looked at this extensively and have come to the conclusion that HCF90 mc cable can be used for the Emergency circuit in a Nursing home. 517.30.C.3(1) applys to hospitals only.

Any comments?


As long as 517.40(B) doesn't apply, and 517.45 (B) or (C) doesn't apply, then I would agree.
 
What about OSHPD 3 Clinics

What about OSHPD 3 Clinics

Thank you very much for the response, and agreeing. This conversation has exploded here and now we wonder how it applies to a OSHPD 3 clinic. It is still not a hospital.
 