517.30(c)

Status
Not open for further replies.

bcngtr

Member
Where a 150kva maximum demand is calculated and 1 transfer switch is used to serve the equipment system, critical branch, and life safety branch, does the equipment system branch circuits need to emanate from a different panel (cabinet) than the critical branch and life safety branch? I interpret Figure 517.30, No. 2 in the FPN as the equipment system, critical branch and life safety branch as being fed from the same buss as this is my interpretation of the horizontal line.

Our inspector states regardless of the 1 transfer switch allowance, the equipment system must remain separate from the critical and life safety branches as per 517.30(C)(1). He is requring a separate panel to be installed fed from the panel that serves the critical branch and life safety branch.
 