517.31(B)

Status
Not open for further replies.

m sleem

Exemplary Сasual Dating - Genuine Females
Location
Usa
Occupation
Health
I am in a situation where there is existing design for hospital need to be rectified in order to meet NEC requirements, the whole essential branch is currently supplied by common BusDuct system through one ATS without segregation between emergency branches as required in code,

In order to rectify the design without replacing the BusDuct system, can we keep the BusDuct system supplied by normal supply only (ATS to be removed) and for each #3 floors there will be tap off point (plug in) supplies one ATS feeding the three branches (life safety, critical, equipment) as long as it has 150 kva or less?
 

david

Senior Member
Location
Pennsylvania
I am in a situation where there is existing design for hospital need to be rectified in order to meet NEC requirements, the whole essential branch is currently supplied by common BusDuct system through one ATS without segregation between emergency branches as required in code,

In order to rectify the design without replacing the BusDuct system, can we keep the BusDuct system supplied by normal supply only (ATS to be removed) and for each #3 floors there will be tap off point (plug in) supplies one ATS feeding the three branches (life safety, critical, equipment) as long as it has 150 kva or less?

IMO, No
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
The 150 KVA limit is for an entire facility, not just for each ATS.

So I also agree - not allowed.
 

kwired

Electron manager
Location
NE Nebraska
It's confusing, how a hospital has less than 150 kva emergency loads?,
Small hospital?

Don't remember size of generator at a small town hospital I used to do work at was, but only had a 200A 208/120 feeder supplied by it, so likely 75kVA or less.
 