I just went over this subject in class and this is what I understand, please someone correct me if I?m wrong.
Long story short, the term emergency system where used throughout the NEC typically mandates application of requirements in Article 700, as in 517.26 for essential electrical systems(nec2011), at the same time the NFPA99 Health Care Facilities Code also has requirements for the health care facility essential electrical system, many of which were not consistent with Art.700, For that reason and to promote consistency between both NFPA 70 & 99 the term emergency and it?s definition was deleted and in some cases replaced with the term essential electrical system in Art.517 in the NEC2014.
In 517.30(B)(1) (2011) the essential electrical system was comprised of the emergency system ( which included the life safety branch and the critical branch) and the equipment system (or equipment branch).
In 517.30(B)(1) (2014) there are no emergency or equipment systems, however there are 3 required branches, life safety, critical and equipment, which are basically the same.
In 517.26 (2014) only the life safety branch and not the entire essential electrical system is required to meet the requirements of Art.700 except as amended in Art. 517.
With that being said, generally speaking Article 700 should still apply for emergency systems installed in buildings other than health care facilities, except as amended somewhere else.
Now, to answer to your question (and this is just me) only the power sources from 517.35(B) or 517.44(B) can be considered as alternate power sources for hospitals or nursing homes and limited care facilities, which in many cases some of this sources could also fall under 700.12