Upon reviewing the NEC 517, I see that the code requires multiple things if there is a "patient bed".

However, I am looking to build a new Medical Office for outpatient exams only. No invasive procedures, patients will not be in the office more than a few hours; no patients will be bedded. General physical exams only.

I spoke with my local township permitting office who indicated my electrical wiring needs to meet NEC 517, but did not specify if my use of the office meets the NEC 517 definition. I searched the forums and see that prior to 2020, it would not meet the definition. However, after 2020, it is unclear.

What do you recommend for "patient exam" rooms in a pediatrician's office? Yes, I will make all the outlets tamper resistant/proof. Do I also need to change all the wiring and add multiple receptacles? Has anyone encountered this issue? Is there a document that would help the inspector understand the requirements?

Thank you.
 

hbiss

EC, Westchester, New York NEC: 2014
Location
Hawthorne, New York NEC: 2014
Occupation
EC
See 517.13 which requires HCF cables in the patent care areas for all branch circuits except for the luminaries and switches outside the patient care area. Receptacles do not have to be hospital grade but it's highly recommended. They also do not have to be TR.

Other areas such as offices, reception desk, waiting rooms, restrooms and hallways can be wired normally. Waiting rooms need to have TR receptacles.