H Hendrix Senior Member Location New England Aug 13, 2014 #1 Does the article tell us that a meter can be installed anywhere w/o a disconnect as long as there is a disconnect within 30' of the structure?
Does the article tell us that a meter can be installed anywhere w/o a disconnect as long as there is a disconnect within 30' of the structure?
D david Senior Member Location Pennsylvania Aug 13, 2014 #2 The service equipment is not required to be at the meter location. edit: Most utilities will still require a grounding electrode at the meter location usually in the form of two ground rods Last edited: Aug 13, 2014
The service equipment is not required to be at the meter location. edit: Most utilities will still require a grounding electrode at the meter location usually in the form of two ground rods