Okay Dealing with a Manufactured home.
So 550.11A deals with the Disconnect that is near a point of entry to the Manufactured home. Requires the 24" to bottom of the panel.
550.30 F is for Service and feeders. Only height requirement is for MOBILE homes 24" not for manufactured homes.
SO currently I have a set up were its serves as both the Service disconnect and the Disconnecting means for the manufactured home. The set up is only 12" from the ground.
I have to run a new line and I will have another disconnect closer to the home. Their current set up is 150' away.
Now I have a Service disconnect and a disconnect for nearest point of entry.
So since the current setup is now just a Service disconnect and not does not serve the function for 550.11 that service disconnect no longer has to meet the 24" requirement cause its a Manufacted home not a Mobile home.
So 550.11A deals with the Disconnect that is near a point of entry to the Manufactured home. Requires the 24" to bottom of the panel.
550.30 F is for Service and feeders. Only height requirement is for MOBILE homes 24" not for manufactured homes.
SO currently I have a set up were its serves as both the Service disconnect and the Disconnecting means for the manufactured home. The set up is only 12" from the ground.
I have to run a new line and I will have another disconnect closer to the home. Their current set up is 150' away.
Now I have a Service disconnect and a disconnect for nearest point of entry.
So since the current setup is now just a Service disconnect and not does not serve the function for 550.11 that service disconnect no longer has to meet the 24" requirement cause its a Manufacted home not a Mobile home.