- Location
- Lockport, IL
- Occupation
- Semi-Retired Electrical Engineer
Existing marina with very old panels is contemplating upgrades. AHJ is likely to invoke ground fault protection (30ma) requirement (new in 2011 NEC, reduced from 100 ma to 30 ma in 2017). I need to tell the marina owners what to expect. How do we add such protection?
- How is this different (meaning equipment, not just setpoint) from the GFCI breakers we might install in a residence?
- Are breakers that have this feature significantly larger (wider) than the existing breakers, so that we may have to replace panels, not just breakers?
- 555.3 applies to feeders also. The only feeders in the marina are protected by fused disconnects. I believe these would have to be replaced, either by enclosed breakers with ground fault protection or with fused disconnects that include a relay that can kick open the disconnect on a ground fault condition. Is there another way?