Hi,
We have to add a 15kva, 575V to 480V transformer to one of our standard machines and I'm fusing the primary and secondary. Here are the calculations I used:
15000/600 = 25 amps.
25*250% = 62.5 amps
I would have to go to the next fuse size which is 70 amp for the primary fuses.
The secondary would be as follows:
15000/480 = 31.25 amps
31.25*125% = 39.06 amps
I would have to go to the next fuse size which is 40 amp for the secondary fuses. I just wanted to double check and see if this is correct. 70 amp seems pretty how and now have have to get 100A disconnect instead of our normal 30A.
My next question is, what would the FLA be now for the machine with the added transformer. Does the transformer change my FLA?
Thanks,
Pete Ippolito
We have to add a 15kva, 575V to 480V transformer to one of our standard machines and I'm fusing the primary and secondary. Here are the calculations I used:
15000/600 = 25 amps.
25*250% = 62.5 amps
I would have to go to the next fuse size which is 70 amp for the primary fuses.
The secondary would be as follows:
15000/480 = 31.25 amps
31.25*125% = 39.06 amps
I would have to go to the next fuse size which is 40 amp for the secondary fuses. I just wanted to double check and see if this is correct. 70 amp seems pretty how and now have have to get 100A disconnect instead of our normal 30A.
My next question is, what would the FLA be now for the machine with the added transformer. Does the transformer change my FLA?
Thanks,
Pete Ippolito